Posts posted by Gabriel Franco

  1. 21 hours ago, keklon said:

    I  need to have  some safeguards in place for the case of an open TC. When the Thermocouple is unplugged the  HSO is driven 100%. I see an red indicator appear on the IO-ATC8 . Is this reported to the control in a SB or do I need to write a net and do a range comparison with upper and lower limits?

    Take a look to the module specs. It shows register values when analog input is out of range.

    https://myzone-kza3sadj.netdna-ssl.com/wp-content/uploads/2015/12/IO-ATC8.pdf

  2. For settings, if those are saved as registers, you may use "Export PLC Operands to Text File" under Connection menu. I use to save operands file together with VLP and OS files as a full backup of my applications.

  3. On 2/28/2019 at 5:03 AM, Wastle said:

    There are sources of electromagnetic fields, but it doesn't bother the other systems.  I have already changed the module.

    Out of interest(newbie here) I am assuming the calibration settings are stored in the CPU which is located in the HMI.

    Calibration data keeps on IO-LCx module.