HughJooters Posted January 10, 2014 Report Share Posted January 10, 2014 Im sure this is an easy one, but my first time using unitronics so here goes. I have a v1040 and i purchased the add on ethernet card. Card is installed and appears to be happy looking at the status bits. My program works fine, i only wanted the ethernet card to be able to remote download updates to my data table. I am unable to ping the PLC. Both my PLC and the card are set for same subnet. PLC - 10.1.6.2 - 255.255.255.0 - 10.1.6.254 PC - 10.1.6.54 - 255.255.255.0 - 10.1.6.254 I think im screwed up in the cards socket init settings, but i havent been able to locate a decent how to on how to set up. Im attaching a couple pics here. Thanks for any assistance. Quote Link to comment Share on other sites More sharing options...
MVP 2022 Joe Tauser Posted January 12, 2014 MVP 2022 Report Share Posted January 12, 2014 You don't have to do a socket init for basic programming - socket 2 defaults to where it should be. You didn't expand your card init so we can't see what's in it. Can you post your program? Joe T. Quote Link to comment Share on other sites More sharing options...
George Young Posted January 12, 2014 Report Share Posted January 12, 2014 Add another socket for protocol ICMP Pings are ICMP protocol TCPSockets.vlp Quote Link to comment Share on other sites More sharing options...
MVP 2022 Flex727 Posted January 12, 2014 MVP 2022 Report Share Posted January 12, 2014 As Joe said, no need to initialize Socket 2 - it's already set to communicate with your PC. Make sure of the following: 1) NAME the PLC with the Set PLC Name function block tied to a Power-Up contact (SB1) Should be SB 2. 2) Address both PLC and PC to the same subnet and make sure there aren't any duplicate addresses. (Looks like you've done that) 3) Use a CROSSOVER cable or an ethernet switch between the PC and PLC. 4) Go to Connection / Communication & OS (or CTRL-F9), - Select Connection Type TCP/IP (Call) - Click on Project Settings and enter the correct IP Address for the PLC, Protocol TCP, Port Number 20256, and the correct PLC Name. Click OK. 5) Confirm settings work by clicking the "Get PLC Information" button. Quote Link to comment Share on other sites More sharing options...
MVP 2014 Simon Posted January 12, 2014 MVP 2014 Report Share Posted January 12, 2014 Further comment, to ping the PLC from the PC, you don't need to set up an ICMP socket on the PLC. It should respond to ping requests in its default state. As far as I am aware the ICMP socket setup is only needed if you want to ping another device from the PLC. If you aren't getting a ping response then there is something wrong at points 2 or 3 of Flex727's post above. If you have added TCP Socket Init blocks I would remove them (but leave the Card Init in place), because, as several have posted above, the default socket configuraiton will respond to PC communication requests. Removing any blocks you have added will ensure you have the default configuration. Re-download and cycle power to the PLC. Also make sure your initialisations are triggered with one-shots, not "always on" conditions. Also try disabling your PC firewall (if you have one). 1 Quote Link to comment Share on other sites More sharing options...
MVP 2014 Simon Posted January 12, 2014 MVP 2014 Report Share Posted January 12, 2014 Sorry, just looked at your screenshots, realised that some of my comments are moot, in particular, you have used a transitional contact for the inits even thought you have added a socket init, it matches the default settings, so it should work fine (though I would still suggest deleting it and relying on the default setup, for simplicity). 1 Quote Link to comment Share on other sites More sharing options...
HughJooters Posted January 13, 2014 Author Report Share Posted January 13, 2014 Thanks all for the responses. As expected it was something simple, i only needed to do a hard power cycle on the PLC. Help much appreciated. H Quote Link to comment Share on other sites More sharing options...