MVP 2023 Flex727 Posted August 10, 2014 MVP 2023 Report Share Posted August 10, 2014 I've been working with Unitronics PLCs for nearly 5 years and one thing has always frustrated me - all 3 timers decrement. When I want to have a simple display of elapsed time (e.g. the time a valve has been open or a pump has been running), there is no simple way that I can see to display that information without a lot of convoluted ladder logic. Have I been missing something all this time? Experienced Visilogic programmers: surely you have this same need from time-to-time - how do you approach it? Link to comment Share on other sites More sharing options...
EduMarg Posted August 10, 2014 Report Share Posted August 10, 2014 Hi Flex727. In the VIsion PLC HMI configuration, when selecting a Timer display variable you can choose to view the elaps time or the or the ramaining time. I think this is what you whant Link to comment Share on other sites More sharing options...
MVP 2023 Flex727 Posted August 10, 2014 Author MVP 2023 Report Share Posted August 10, 2014 Thank you! You know, I think I knew that and was having a senior moment. Link to comment Share on other sites More sharing options...
Cara Bereck Levy Posted August 18, 2014 Report Share Posted August 18, 2014 Flex--I really empathize. The worst is when you know you know this, but still can't remember :-) 1 Link to comment Share on other sites More sharing options...