Vidmas30 Posted April 11, 2019 Report Share Posted April 11, 2019 Hi, everybody, We have strange situation - we prepared Jazz PLC (JZ20-J-T40) for local boiler room control and for data collection to BMS system (for that we configured Jazz as a slave with JZ-RS4 comm module (RS-485)). BMS was made by other company(they used Schneider SmartX controller AS-P). They get all the information, but in our cabinet all LED pilot lights and LED indication lights of relays that connected to PLC's outputs are flickering. If we disconnect modbus cable, everything is fine. When connect back - LEDs flickers. BMS company (their modbus cable) says the cable is fine, properly grounded and etc. What could be the cause of that strange behaviour and what could we do to prevent that? Thank you! Quote Link to comment Share on other sites More sharing options...
MVP 2022 Ausman Posted April 11, 2019 MVP 2022 Report Share Posted April 11, 2019 It definitely sounds like an incorrect power configuration issue. Amongst other possibilities, the flicker could be your power supply constantly approaching it's shutdown limit, but not quite getting there. I'd check a few things. 1). Are the 2 systems being powered from different phases of a 3 phase supply? I ALWAYS ensure that all controls are on the same phase. And associated with this, ensure that the neutral to your gear's location is ok as well, and the actual volts at your end are correct. 2). Have you got the modbus cable earthed at your end? If so, if you connect, but with the earth disconnected, does the problem go away? 3). If the problem persists after checking 1 & 2, measure the current draw on your power supply with a good quick acting DC clamp directly at the output, with your system running with and without the modbus cable connected. If you can't get a good enough DC clamp, put an analogue ammeter in the line. If you find that there is a significant difference, then there is definitely a power interaction issue. Tracking the difference down the various branches will help pinpoint things. cheers, Aus Quote Link to comment Share on other sites More sharing options...
MVP 2022 Joe Tauser Posted April 12, 2019 MVP 2022 Report Share Posted April 12, 2019 I don't think the JZ-RS4 is isolated. You're probably connecting your 0V terminal to their ground via the communication cable. Connect 0V from your system to the common on the DC power supply in their system with a wire and see what happens. Joe T. Quote Link to comment Share on other sites More sharing options...
MVP 2022 Ausman Posted April 13, 2019 MVP 2022 Report Share Posted April 13, 2019 Just to clarify, ALL LEDS, not just those on the plc gear, ALL indicators, flicker? Are the pilots driven from the PLC call, or from the controlled contacts closing? Big difference. I'm also with Joe on his suggestion, had not considered this. cheers, Aus Quote Link to comment Share on other sites More sharing options...
Recommended Posts
Join the conversation
You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.