 We have strange situation - we prepared Jazz PLC (JZ20-J-T40) for local boiler room control and for data collection to BMS system (for that we configured Jazz as a slave with JZ-RS4 comm module (RS-485)). BMS was made by other company(they used Schneider SmartX controller AS-P). They get all the information, but in our cabinet all LED pilot lights and LED indication lights of relays that connected to PLC's outputs are flickering. If we disconnect modbus cable, everything is fine. When connect back - LEDs flickers. BMS company (their modbus cable) says the cable is fine, properly grounded and etc. What could be the cause of that strange behaviour and what could we do to prevent that? Thank you!

Link to comment
Share on other sites

  • MVP 2023

It definitely sounds like an incorrect power configuration issue.  Amongst other possibilities, the flicker could be your power supply constantly approaching it's shutdown limit, but not quite getting there.  I'd check a few things.

1).   Are the 2 systems being powered from different phases of a 3 phase supply?   I ALWAYS ensure that all controls are on the same phase.  And associated with this, ensure that the neutral to your gear's location is ok as well, and the actual volts at your end are correct.

2).  Have you got the modbus cable earthed at your end?  If so, if you connect, but with the earth disconnected, does the problem go away?

3).  If the problem persists after checking 1 & 2, measure the current draw on your power supply with a good quick acting DC clamp directly at the output, with your system running with and without the modbus cable connected.  If you can't get a good enough DC clamp, put an analogue ammeter in the line.  If you find that there is a significant difference, then there is definitely a power interaction issue.   Tracking the difference down the various branches will help pinpoint things.

cheers, Aus

Link to comment
Share on other sites

  • MVP 2023

Just to clarify,  ALL LEDS, not just those on the plc gear, ALL indicators, flicker?  Are the pilots driven from the PLC call, or from the controlled contacts closing?  Big difference.

I'm also with Joe on his suggestion, had not considered this.

cheers, Aus

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...