The  Main Program scans the nets from   net 1(Top)   to  Net  X(End)   - Top to Bottom - , deviating only to do called subroutines.

When a Contact Output is used multiple times in the program,   Only the  LAST   Time  Used  Counts because that is when the Scan does the final  determination of the condition of the contact Output  before setting the outputs,  doing housekeeping  and restarting the scan again.

Where else is MB 64 being used?

Subroutines are only  Active when CALLED, otherwise, the subroutine  and all it's internal logic  is ignored.

Dant

 

 

Link to comment
Share on other sites

  • MVP 2023

And to end all those good comments above this one, all those warnings in the bottom of your screenshot fully explain part of the issue.   Split your nets up so that you only have one coil per net.  Just because it works in one area doesn't mean it is good practice.  Remember that even though the graphical presentation shown to you looks like it will work, the plc might approach it far differently, so the reference to Stl is very relevant.

All your "controls" on the left of the rung can be tallied together near the beginning of your program, controlling a batch of MBs that you use instead.  You enter all your controlling parameters and then will likely be surprised at how many have commonality. This method will likely actually decrease the number of ladder elements, even doing the one coil per net, as you only have the derived MB as the input. 

Learn about some system delays involving HMI screens. 

Is MB70 actually being turned on?  We are assuming that MB70 and MB45 are associated to different displays.

cheers, Aus

Link to comment
Share on other sites

  • 4 weeks later...
On 4/26/2019 at 10:53 PM, kratmel said:

Please  Find MB64  in your program and post result to the topic.

find.JPG

 

On 4/27/2019 at 12:06 AM, Ausman said:

And to end all those good comments above this one, all those warnings in the bottom of your screenshot fully explain part of the issue.   Split your nets up so that you only have one coil per net.  Just because it works in one area doesn't mean it is good practice.  Remember that even though the graphical presentation shown to you looks like it will work, the plc might approach it far differently, so the reference to Stl is very relevant.

All your "controls" on the left of the rung can be tallied together near the beginning of your program, controlling a batch of MBs that you use instead.  You enter all your controlling parameters and then will likely be surprised at how many have commonality. This method will likely actually decrease the number of ladder elements, even doing the one coil per net, as you only have the derived MB as the input. 

Learn about some system delays involving HMI screens. 

Is MB70 actually being turned on?  We are assuming that MB70 and MB45 are associated to different displays.

cheers, Aus

Thanks, yes MB70 and MB45 does come ON when I go to the different displays

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...