GioSerrano Posted May 4, 2020 Report Posted May 4, 2020 How can i get sure, how many analog inputs may we configure for a Vision V570 o a Vision V130. I'got 20 units of IO-AI8, some I have 160 analog inputs, 4-20mA and 0-10Vdc. Can a I use V570 ? taking into account memory program capacity?
MVP 2023 Ausman Posted May 4, 2020 MVP 2023 Report Posted May 4, 2020 I can't immediately find the specifications for limits, but the easy way to check is to use Hardware Configuration. Simply load up all the I/Os you want to use, and at the bottom of the window is the report on the capacity used. But I do recall some issues with this report in the past. Can someone also please remind me where the specs are squirrelled away! cheers, Aus
Gabriel Franco Posted May 4, 2020 Report Posted May 4, 2020 48 analog inputs per EX-A2X or EX-RC1, 6 IO-AI8. It is because data bus capacity, not PLC memory, if I remember well (from support answer I got time ago). 1
MVP 2023 Joe Tauser Posted May 7, 2020 MVP 2023 Report Posted May 7, 2020 You need to go into CANbus land using EX-RC1s for this one, even if it's in the same panel. Each EX-RC1 can support 8 modules. I just did a test configuration with 8 IO-AI8s, which will give you 64 inputs per drop. You can have up to 59 EX-RC1s talking to one master, although I've never personally done more than 4. Joe T.