Hello friends.
I am using a PLC communicating with an UAC CB 01RS4.

What I want to achieve is an meter MODBUS measuring the volt and amp value of a load, connected to a PLC via Modbus, this PLC is connected to a computer via ethernet.
I managed to establish communication but didn't suceed. Indeed, All attempted sessions are fails and the status is 3  - Connection exists, but there is an error in the MODBUS commands.
I have added the MODBUS module to the PLC on UniLogic, and all informations (Modbus panel, baud rate, data bit....) are correct.

Then I've added a Master -> 'registers periodic' -> the modbus communication is the UAC-CB-RS4 and the adress is 5000 (which is the adress register of the Voltage measurement content (for the automate). I also tried to add a slave but still I have the same errors.

If you have any clue on why I have a connection but the MODBUS command has errors, please tell me 😀.

Thank you very much !!

 

 

Link to comment
Share on other sites

  • StageAge54 changed the title to Trying to get infos from a Voltmeter connected to a MODBUS
  • MVP 2023

Gabriel and Kratmel, does Unistream stuff also do the register number offset of 1 that Vision does?  Perhaps this is the issue?

And Stage, trial your comms using a PC first, then once proven transfer the known good parameters to the PLC's commands.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...