4 minutes ago, kratmel said:

What sensor model you try to use?

This is important because the jumpers default to voltage (0-10V input). If you are using current (0-20mA or 4-20mA) you must set the jumpers properly. Also, be sure you have a good power supply (must be 24V even though the PLC itself can run on 12-24V) and confirm your settings in the PLC program Hardware Configuration.

1 hour ago, Tom P said:

all I get is a value of 1730

Do you have your hardware config set to 12-bit or 14-bit?

Link to comment
Share on other sites

PTD25-20-0100WCH       I found out that the sensor that I am trying to hook up is for 4-20mA output. The programmer is going to have to re-vamp the program for the 4-20mA signal.  Thank you for your answers. I think I found the problem and know what has to be done.  Thank you again.