micapp Posted August 13 Report Share Posted August 13 I have 2 USP-156-X10 with CPU attached. Sometimes the HMI does not respond to touch. If I remove power and reconnect, it is working OK. Is there a reason for this? Is there any shortcut to restart onlly HMI? The PLC cannot be restarted due to application. Quote Link to comment Share on other sites More sharing options...
MVP 2022 kratmel Posted August 13 MVP 2022 Report Share Posted August 13 2 hours ago, micapp said: Is there a reason for this? Is it VFD or other source of EMI present in application? You can find on forum recomendation about proper grounding and solution for EMI problems. Quote Link to comment Share on other sites More sharing options...
AlexUT Posted August 14 Report Share Posted August 14 Check how Actions are activated. Actions should be one-time activated. Either positive, negative transition. Quote Link to comment Share on other sites More sharing options...
micapp Posted August 26 Author Report Share Posted August 26 Sorry for late reply: Yes there is hih powers controlled with triacs and thyristors, etc (VFD, UPS, UV-ballasts). I thought maybe this might be a problem yes. My actions is either flanks or buttons with press=set bit, release=reset bit Quote Link to comment Share on other sites More sharing options...