Hello,

i have a v700 plc with a v200-18-e4xb module.

i want to use a thermocouple with it.

i've configured visilogic with "T/C type J, no filter, mode °C, OP MI1" (see picture)

i wired it on the analog channel t- and t+

0 andVA are ok with 24vdc (digitals input and output, analog output are ok and functional)

i've set the jumper 3,4,5,6,7,8 on the B position

but when i power on, the MI is 32767

Someone can help me to found why doesn't works ?

thanks

Josselin

 

 

 

visi1.JPG

20180413_130827.jpg

Link to comment
Share on other sites

Hello, thanks for answers !

Yes i removed thermocouples'wires for picture. It's to show all other things are ok.

i've used t- and t+ for channels 0 and 1. i tryed to reverse wires but nothing's better.

withe wire on the t- and black wire on the t+

I read the doc and understand that input value deviates greatly but why ?

i don't see where the 12 or 14 bits resolution may be selected by software (point 7 of the doc)... maybe that's the pb...

an idea ?

Joss

 

 

Link to comment
Share on other sites

  • MVP 2023
2 hours ago, Joss said:

i don't see where the 12 or 14 bits resolution may be selected by software (point 7 of the doc).

That's only for the 0-10V, 0-20mA, & 4-20mA analog inputs. It doesn't apply to thermocouples. Thermocouples have resolution to a tenth of a degree.

Link to comment
Share on other sites

  • MVP 2023

You've already mentioned that you set the jumpers - they are correct. 

Verify you have +24V on terminals VA and 0V on the other side of the module.

As a sanity check, put a jumper wire between T+ and T- on channels 0 and 1.  This should give you ambient temperature in tenths of a degree.

Let us know.

Joe T.

Link to comment
Share on other sites

Hello !

Everything is ok !

Another guy working with me on the project unplugged the 0V wire on the power after the first tests with analogic outputs... so thermocouples wiring doesn't work.

We modified this and now, all is functional.

Use the thermocouples values is easy with visilogic.

Thanks for help

Josselin

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...