Having issues getting an arduino sensor to read properly on a V350-35-RA22 despite it being a simple 0-10v signal.
Title basically says the whole issue. I'm trying to get a usable reading from the sensor listed below, but it just seems to fluctuate between 2 and 3 volts even if nothing is plugged in. So my question is two-fold. Can I get a signal that is more precise than a whole number, and will that sensor even work with a PLC and if not is there anything I can get to interface the two?
Sensor - https://www.dfrobot.com/wiki/index.php/Turbidity_sensor_SKU:_SEN0189
Thank you very much for your time/help.
According to your link, the sensor output is only 0-4.5 volts. However, you should be able to make that work. The standard analog input on hte V350-35-RA22 has 14-bit resolution, which even at half scale will still give you at least 2 or 3 decimal places of precision. How are you measuring the 2-3 volts you say you are getting? Is this a direct measurement with a voltmeter, or are you linearizing the analog input on the PLC?
If you have access to a 0-10V source you can inject a signal and see if it is a code/config issue or the device. Ramping up and down the scale will give you a change in your PLC value. In the absence of a source you can even use batteries 1.5/3V/6V/9V
Some likely things to check:
  • Dip switch settings are correct as per install manual for 0-10V
  • Hardware config settings are right
  • Any scaling in your code is correct for the bit resolution of your model
  • 0V connections as per manual
The help files and examples are always worth looking at
Direct reading through the MI that the analog input is going to. No matter what I do it only gives whole value readings of 1-4.
I've checked all that a few times now, I'm just trying to test this sensor so there isn't much actual logic involved. Jumpers are all correct and all that.
That's basically zero. The value you should see on the MI is 0-16,383, which is scaled to 0-10V (i.e. 1V = 1638, 5V = 8191, 10V = 16383).
Yes....but what is the actual reading at the connections at the plc using a voltmeter?  As Flex says, the MI0 is essentially indicating nothing is there at all.  As C_R says, check connections, especially that your 0V are commoned correctly.
And visiting this again, I think I see where your fundamental thinking is astray.  I have a feeling that you are expecting to see MI0 showing the actual voltage.  It doesn't work that way, it works the way Flex has pointed out in that analogue inputs generate numbers b/n a range, dependent on speed of read and type of input.
And I still want you to use a voltmeter!
Okay, sorry for the late response. New day new voltmeter approach.
So with a voltmeter I get .756 volts when the sensor is clear and .950 volts when the sensor is covered.
Could it have something to do with the setup that I'm using to power it? I have a variable voltage output powering the sensor itself because it has to be set to 5V, so the positive and negatives are coming from that machine instead of the PLC.