Blitz Posted June 5, 2011 Report Posted June 5, 2011 I seem to have bumped to an undocumented limitations on I/O expansion module count per adapter (EX-A1 or EX-RC1). The hardware configurator allows us to place 8 ATC8 modules on the rail without error. (Also, note that with 8 ATC8, the 5Vdc power limit is not exceeded). However, we get an error message when we try to configure the entire 64 channels available. . The error start to appear on the 50th channel. Actually, when mixing a combination of digital and analog I/O modules, the limit appears to be 50 words. If 50 IO words is actually the limit, then it should appear on the documentations as it is an important information for sizing the PLC. We need the entire 64 AI channels per rail. Is there any work around aside from adding another adapter module? Thanks.
Stein Yair Posted June 15, 2011 Report Posted June 15, 2011 Hi, Unfortunately, there is no workaround this limitation. You need to add another adapter. Note that there is an indication of the IO Capacity at the bottom of the Hardware Configuration window.
Rene Posted August 13, 2013 Report Posted August 13, 2013 This limitation (actually there is possibility to use only 49 analog I/O points) MUST be mentioned in documentation and brochures. So the V1040 and V1200 MUST have more I/O capacity, 49 I/O words is not much. There is 64 I/O words needed!
Emil Posted August 13, 2013 Report Posted August 13, 2013 Two notes: 1. "Limitation" CANNOT be metioned in any documentation, as it depends on many factors. This number comes from limitation in communication between PLC and EX-A2X. As Yair stated in his post above, in bottom line of Hardware configuraiton window (VisiLogic) there is a "calculator" of communication load. Any one can check before starting to build his project. 2. In fact, there is no such limitation! You can add Remote adapters EX-RC1. To each adaprer you can connect, let's say 6 x IO-ATC8 = 48 universal 14 bit AI. You can connect up to 60 x EX-RC1 to one PLC. This means - 60 x 48 (via RC1) + 48 (on A2X). In my calculator the number is 2928. You can add another few analog I/O on board or Snap In module, but this will not change the final situaiton drastically. BTW - having 6 x ATC8/AI8 ot each adapter, you can still add up to 2 more I/O modules with digital I/O...
Gabriel Franco Posted August 13, 2013 Report Posted August 13, 2013 As I understand the issue, there is a 50 words limitation for local I/O expansión. 16 points digital input or output uses 1 word, so, one can mix any cards as long as they do not exceed such limit. Am I correct? I tried 6xATC8/AI8 + 1xIO-DI16 + 1xIO-TO16 and calculator shows 100% capacity, but also got same error of original post
Emil Posted August 13, 2013 Report Posted August 13, 2013 UniCAN can transfer 32bit at one package. In this matter you're right. But there is no problem to send thhe data in several packages. It will be slower, but if you transfer analog values, which don't change so fast, it will be more than good enough.