gerard339 Posted December 13, 2019 Report Share Posted December 13, 2019 Hi, I am using a current simulator to input a 4-20mA signal to AI0 of a IO-A14-AO2. The raw data is doing the opposite of what I am expecting. As I increase the current, the raw data decreases, and visa-versa: the value of MI 0 goes down as mA input signal goes up. I tried reersing the signals but it does not work either - do you have any idea what may be happening here? I tried it with both current and voltage signals. Quote Link to comment Share on other sites More sharing options...
MVP 2021 Flex727 Posted December 14, 2019 MVP 2021 Report Share Posted December 14, 2019 Did you try actually measuring the current with multimeter? Quote Link to comment Share on other sites More sharing options...
TozoM8 Posted December 15, 2019 Report Share Posted December 15, 2019 AI0 looks like voltage input. AI1-3 is current if I read it correctly. https://myzone-kza3sadj.netdna-ssl.com/wp-content/uploads/2015/12/IO-A14-AO2-5408-0061-2.pdf Quote Link to comment Share on other sites More sharing options...
sgull Posted December 15, 2019 Report Share Posted December 15, 2019 AI0 to AI3 can be wired as voltage or current inputs. For current connect the 4-20ma to "I" and the 0v to "COM" Make sure that the 0v of the transmitter is common to the 0v of the input module power supply Quote Link to comment Share on other sites More sharing options...