Dermie Posted January 22, 2022 Report Share Posted January 22, 2022 I can not change a variable on the hmi. I have MI 61 setup on one page and it allows me to change the value from the HMI. I have what looks the same setup on another page and it will not let me change the variable. They look to be setup on each page but one page will not let me change the setpoint.the one with the increment of 11 does not work. any help would be appreciated. cheers wayne Link to comment Share on other sites More sharing options...
MVP 2023 kratmel Posted January 22, 2022 MVP 2023 Report Share Posted January 22, 2022 Min value is 120 > max value 5. It is strange. Link to comment Share on other sites More sharing options...
Dermie Posted January 22, 2022 Author Report Share Posted January 22, 2022 Thank you, some times you can not see the obvious. Link to comment Share on other sites More sharing options...
MVP 2023 Ausman Posted January 22, 2022 MVP 2023 Report Share Posted January 22, 2022 And why 2 screens setting the same MI anyway? 🤔 Link to comment Share on other sites More sharing options...
TozoM8 Posted January 27, 2022 Report Share Posted January 27, 2022 I would think one for operator, the other for the admin on a password screen. Link to comment Share on other sites More sharing options...