Bruce Booska Posted February 17, 2022 Report Posted February 17, 2022 I added a "List of Images Variable" and linked 15 different images in it to 15 different alarm bits, each with its own rung and conditions and for some reason all of them are being forced on regardless of it's rung conditions. I can't even force them off. Anybody seen this before? I've included pictures
sgull Posted February 17, 2022 Report Posted February 17, 2022 If you connect a coil directly to the left power rail it will always be on. use a contact of the coil to store the value. 1
MVP 2023 Flex727 Posted February 17, 2022 MVP 2023 Report Posted February 17, 2022 Good catch sgull! I don't know how many times I've accidentally grabbed a coil instead of a contact and then couldn't figure out why my logic didn't work. This is easy to do and the OP certainly copied the mistake to all of the other rungs.
Dave Posted February 17, 2022 Report Posted February 17, 2022 Good catch indeed. I was in the process of duplicating the logic and wasn't having any issues...but i didn't even notice the coils instead of contacts and used contacts in my version. I guess my brain just interpreted the coils as contacts.