Jesse Posted April 27, 2022 Report Share Posted April 27, 2022 We have a V130-J-TR6 with an ethernet card installed. I have followed all of the examples and youtube videos but I still can't seem to get our iFix software to communicate. We are able to ping the ip address successfully but we still have a communications failure. I have attached my code. One thing that I found inconsistent about some example projects and youtube videos is that some run a "socket init" FB and some don't. I have tried both ways unsuccessfully. All we want to get from the PLC to SCADA is the Filter level, Turbidity, and LOH. (MI 17, MI 27, and MI 37) Any other suggestions to the code is acceptable as well. Filter Level Display_V4_Comms.vlp Link to comment Share on other sites More sharing options...
DanT Posted April 27, 2022 Report Share Posted April 27, 2022 Hi Jesse; I downloaded your program and have looked it over. A few Comments: 1 You have many nets that have multiple logical statements in them Break them out into individual nets, Look at the STL Quick view. Unitronics ladder processing prefers 1 logical statement to produce 1 finite output from the net, not many logical statements and a confused final output. ( I have seen cases where multiple statements in the same net gave the WRONG output desired, breaking them out into individual nets cleared the problem) Unitronics has no limits for the number of nets in a subroutine. 2. In the !Home Routine, Break up Net 1 into 2 separate nets Store and MB 31 in one Net Com setup in another Net 3. In the !Home Routine , Break up Net 2 into 2 separate nets, Place the Modbus IP Scan in its own net BEFORE calling the Main Subroutine. The way you have it placed is that it will be processed AFTER the Main Subroutine has been processed. 4. In the Admin Password Subroutine Break into 2 separate Nets Change the --| SB54 |---- to a ---| P |--- Leading edge one shot pulse 5. In the Main Subroutine -- Break all those subroutine calls in Net 1 into individual nets, they will still get called in sequence. 6. Unitronics has defaults for setting up the Ethernet Sockets. You can modify them as needed, or restate them in the net to avoid ambiguity ( I do this in my programs) 7. If you want your SCADA to pick up specific data, and it is spread out over different MI's, regroup them together in 1 area to make the Modbus calls easier. ( if you cannot regroup them , then use a STORE to send them to a grouping area) Doing these will help you troubleshoot your connection issues. DanT Link to comment Share on other sites More sharing options...
Fernando Castro Posted April 27, 2022 Report Share Posted April 27, 2022 3 hours ago, Jesse said: I have attached my code. One thing that I found inconsistent about some example projects and youtube videos is that some run a "socket init" FB and some don't. I have tried both ways unsuccessfully. I think you need the socket Init. I have multiple PLCS as Modbus TCP/IP Slaves. and I do the following On power Up first I have an Init sub ruoutine wich looks like this Initialization: (There are more things but only this line is relevant to Network) Then I do the Modbus IP config on power up too I enable Modbus Scan after Modbus Config was executed. Ignore the MBs inbetween (MBs 80,81,82,84), I have some logic just to do a network restart on a specific sequence of steps relevant to my application, but you wont need to do that Quick note, In my experience some unitronics OS have bugs related to protocol communication, so you can try with an older version if still can not communicate. in my case v570 an v700 works with 4.8.10, but I dont know about other PLC models. Link to comment Share on other sites More sharing options...
MVP 2023 Flex727 Posted April 27, 2022 MVP 2023 Report Share Posted April 27, 2022 @Fernando Castro, great response to the post. You appear to organize your setup the same way I do (which is clearly the best way 😉). However, I'm curious why you have an inverted contact for MB 84 in front of your SET coil for the same MB? Link to comment Share on other sites More sharing options...
Fernando Castro Posted April 27, 2022 Report Share Posted April 27, 2022 2 hours ago, Flex727 said: @Fernando Castro, great response to the post. You appear to organize your setup the same way I do (which is clearly the best way 😉). However, I'm curious why you have an inverted contact for MB 84 in front of your SET coil for the same MB? there is some logic involved in order t do a specific sequence later on the code. I am not sure why but for v700 I had this issue on wich the socket got locked? and reconnecting did not work, needed to reset power wich was not a viable option process wise and I need to be able to restart the connection whitout stopping the process, long story short on this sequence MB80 could be active for a couple of scans, I usually use the sets with same contact negated, that way set will only be executed once, ant that once is when it was not set 🤷♂️. I don't like to abuse with the use of set /resets but I want to be sure that the only way I am going to have that set being set is if it wasn't being set already. Link to comment Share on other sites More sharing options...
MVP 2023 Flex727 Posted April 27, 2022 MVP 2023 Report Share Posted April 27, 2022 2 hours ago, Fernando Castro said: but I want to be sure that the only way I am going to have that set being set is if it wasn't being set already. But a SET Coil would do nothing if the bit was already set, no? Link to comment Share on other sites More sharing options...
Fernando Castro Posted April 28, 2022 Report Share Posted April 28, 2022 1 hour ago, Flex727 said: But a SET Coil would do nothing if the bit was already set, no? yes it will, its being used in the other part of the code that Is not shown, a pulsed button triggers the logic of the reconnection, and during that reconnection the program could complete a couple of scans, and then if that NC contact was not there it will proceed to start modbus scan right away, and I don't want that Link to comment Share on other sites More sharing options...
MVP 2023 Flex727 Posted April 28, 2022 MVP 2023 Report Share Posted April 28, 2022 Hmm, I must not understand something because I can't envision any situation where that inverted contact would have any effect. It certainly doesn't hurt anything, but just seems totally unnecessary to me. As I see it, if MB 84 is off, then it will be turned on - with or without the inverted contact. If MB 84 is on, then MB 84 just stays on, with or without the inverted contact. Link to comment Share on other sites More sharing options...
Fernando Castro Posted April 28, 2022 Report Share Posted April 28, 2022 5 hours ago, Flex727 said: Hmm, I must not understand something because I can't envision any situation where that inverted contact would have any effect. It certainly doesn't hurt anything, but just seems totally unnecessary to me. As I see it, if MB 84 is off, then it will be turned on - with or without the inverted contact. If MB 84 is on, then MB 84 just stays on, with or without the inverted contact. I guess you are right 🤔, but I swear there is a use case for something like this,.... after I looked into it again this is not. Link to comment Share on other sites More sharing options...
MVP 2023 Flex727 Posted April 28, 2022 MVP 2023 Report Share Posted April 28, 2022 I seriously thought I might be missing something important. Thanks for double checking. Link to comment Share on other sites More sharing options...
Jesse Posted April 29, 2022 Author Report Share Posted April 29, 2022 Fernando, I have tried the things you listed except for the older OS install. Still no luck. How exactly do you try an older OS? Link to comment Share on other sites More sharing options...
DanT Posted April 29, 2022 Report Share Posted April 29, 2022 Hi Jesse; I looked at your program again and began to edit a few things. You have the PLC name set as an Indirect address MI 0 -- as set up -- the name of the PLC is a NULL ( No Name) You are trying to use a MI Integer as the name, this will not work - I found the screen where you assign the PLC Name - COMMS The name should be an ASCII String, and if you tried to write a name here(MI 0), you will overwrite MI1,MI2, etc. or Invalid ACSII Characters Even if the Name is to be a number, the number is entered as an ASCII String -- Modify your COMM HMI Screen to enter the PLC Name Store the PLC Name some where else - in your program I chose MI 500 Maybe for testing, enter a the PLC Name as a Direct String like V130TR6 The PLC Name acts like a password to access the PLC Look up PLC Name in Help Attached are my revisions -- to the program -- my revisions are in Startup Net and COMMS HMI Just as a note: MI's can be used to store and work with Integer Numbers, and also store and work with ASCII Chars When you use MI's to store ACSII Chars, change the view from DEC to HEX and have an ACSII Table handy DanT 622564519_FilterLevelDisplay_Dan0429A.vlp Link to comment Share on other sites More sharing options...
MVP 2023 Ausman Posted April 29, 2022 MVP 2023 Report Share Posted April 29, 2022 As an aside to perhaps help you understand what Dan is saying, please consider the following. I have recently been writing elsewhere about using the RTC to ASCII function, but the way it works is similar. This is the result in an MI vector of writing the date from the RTC using the function. Note how I've got the data set to display as Hex, which is simply done by left click on the DEC/HEX description cell to alternate b/n the two. The format is written as DD_MM_YY and in this case it is the 24th of April, 2022, so is 24_04_22 using our local naming convention. Now consult the table. If you look at Hx 32 you'll see that it is Chr 2, and Hx 34 is Chr 4. Hex 5F is _ etc. so I'll let you figure out how things are in the MI as Hex to get the full display correct. cheers, Aus Link to comment Share on other sites More sharing options...
Fernando Castro Posted May 2, 2022 Report Share Posted May 2, 2022 On 4/29/2022 at 9:16 AM, DanT said: Hi Jesse; I looked at your program again and began to edit a few things. You have the PLC name set as an Indirect address MI 0 -- as set up -- the name of the PLC is a NULL ( No Name) You are trying to use a MI Integer as the name, this will not work - I found the screen where you assign the PLC Name - COMMS The name should be an ASCII String, and if you tried to write a name here(MI 0), you will overwrite MI1,MI2, etc. or Invalid ACSII Characters Even if the Name is to be a number, the number is entered as an ASCII String -- Modify your COMM HMI Screen to enter the PLC Name Store the PLC Name some where else - in your program I chose MI 500 Maybe for testing, enter a the PLC Name as a Direct String like V130TR6 The PLC Name acts like a password to access the PLC Look up PLC Name in Help Attached are my revisions -- to the program -- my revisions are in Startup Net and COMMS HMI Just as a note: MI's can be used to store and work with Integer Numbers, and also store and work with ASCII Chars When you use MI's to store ACSII Chars, change the view from DEC to HEX and have an ACSII Table handy DanT 622564519_FilterLevelDisplay_Dan0429A.vlp 174.57 kB · 1 download I dont think PLC name should be necessary when trying to establish commuinaction over modbus TCP/IP but, sure the PLC name should be propperly assigned if you want to use other unitronics software that uses ethernet @Jesse you should check that too just to rule out that. On 4/29/2022 at 6:57 AM, Jesse said: Fernando, I have tried the things you listed except for the older OS install. Still no luck. How exactly do you try an older OS? Check this post that from a couple of moths ago, someone had that problem and was the OS, over there is explained how to and wher to download the OS. But before digging more deeply on Unitronics side problems, are you 100% thet the issue is not on the SCADA side, or the network itself? do have any other way to test the modbus communication? I use a CODESYS based virtual PLC on my computer to thest ethernet based communications. I mean, sure it will require time to set it up an learn to use the plataform, but being free I feel is worth it. Link to comment Share on other sites More sharing options...
Jesse Posted May 2, 2022 Author Report Share Posted May 2, 2022 Dan, Fernando thank you. I finally got the issue resolved. After I fixed the "PLC Name", I also noticed the lower part of the "Modbus IP Config". Somehow I missed this part in the manual where you have to input the slave ID and address. I had seen this before but I thought that part was only if you were setting the PLC to be the modbus master. We are going to have 12 of these on line connected to SCADA. 4 sets of 3 of them will be ran to a switch. Does it make since for each one of these to have all 12 lines filled out or do I only need a single line for that particular PLC? My thoughts were that they will all have seperate IP addresses (XXX.XXX.XXX.YY). Where the YY will be different for each and the slave ID will remain the same. The goal here is to use a single code for all 12 V130s then just changing the YY through the HMI. Is this going to be possible? Link to comment Share on other sites More sharing options...
MVP 2023 Flex727 Posted May 2, 2022 MVP 2023 Report Share Posted May 2, 2022 1 hour ago, Jesse said: I had seen this before but I thought that part was only if you were setting the PLC to be the modbus master. This IS only if the PLC is the MODBUS Master. It does not need to be filled out when it is a MODBUS Slave. That was not your problem. 1 hour ago, Jesse said: My thoughts were that they will all have seperate IP addresses (XXX.XXX.XXX.YY). Where the YY will be different for each and the slave ID will remain the same. The goal here is to use a single code for all 12 V130s then just changing the YY through the HMI. Is this going to be possible? Yes, this is absolutely possible. Link to comment Share on other sites More sharing options...
Fernando Castro Posted May 2, 2022 Report Share Posted May 2, 2022 6 hours ago, Flex727 said: This IS only if the PLC is the MODBUS Master. It does not need to be filled out when it is a MODBUS Slave. That was not your problem. I was about to say the same, slaves doesn't need to know other slaves or even the master IP, only the Master needs to know the IP addresses of each device it is going to connect with 8 hours ago, Jesse said: We are going to have 12 of these on line connected to SCADA. 4 sets of 3 of them will be ran to a switch. Does it make since for each one of these to have all 12 lines filled out or do I only need a single line for that particular PLC? My thoughts were that they will all have seperate IP addresses (XXX.XXX.XXX.YY). Where the YY will be different for each and the slave ID will remain the same. The goal here is to use a single code for all 12 V130s then just changing the YY through the HMI. Is this going to be possible? I have like 180 devices, and I set the IP and PLC name on a settings screen on each PLC. So if at some point someone requires to change the IP, or use a different network you won't want to be required to download the program again. at least thats my recommendation, I like to be able to leave work and not to be bothered just because some IP is already taken by another device 😂 As an engineer I knew used to say. "And thats how its done... If you want to go to bed early" 1 Link to comment Share on other sites More sharing options...