How can i remove/ identify this error "Value is not available because the limit for function tags was reached""


Recommended Posts

  • MVP 2023
Posted

I can't see the rest of your project, but it does look like you have quite a few custom controls defined.  There is also a limit on the number of retentive tags you can have, which can get consumed in a hurry if you have large data tables defined as retentive.

Please post your project or submit it to support@unitronics.com.

Joe T.

  • Like 1
  • MVP 2023
Posted

And Nicholas, please don't post the same question twice.  I've removed the identical one from the lounge but left a link there.

All posts on the forum are subject to moderator approval, so there will always be a delay in it appearing correctly.  It hasn't got lost and you don't need to do it again....just wait a bit...mods are worldwide.

cheers, Aus

  • Thanks 1
Posted

I think you misundesrtood the custom controls use. 

You create a single custom control to all valves, other to all pumps, that share the same frame, buttons and layout.  Then, you place the control on the screen (or screens) you need it and set parameters associated with the device (pump, valve, ...) you want to operate.

  • Thanks 1
  • 2 weeks later...
Posted

Here you are using AV_001 as direct coil, it must be direct contact:

image.png.f5a37f39aff7b7cd45bbadbbcace68d1.png

 

IP address is missing for remote slave1:

image.png.d5d1b47aeae7a75b23a0aacce9244fe7.png

 

PLC is acting as Modbus TCP server or client? You set both modes up.

 

Active bits are missing in coils periodic task.

 

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.