Hello all,

 

I have question related to connecting Vision 280 with Modbus TCP zenon SCADA driver. I have experience with other PLC-s but not with Unitronics.

Please find attached config below:

image.png.792632fadc344e817c8df16b01c9d0e6.png

Below you can see zenon driver config and one variable config. I tried to see ML12 from program. Is this the way to directly call adress from SCADA or I missed some step?

sigma is PLC name, PLC IP is in range of PLC.

image.thumb.png.4a7baa6c62f0685e97c0aa6254be8df0.png

Link to comment
Share on other sites

On 9/19/2023 at 9:35 AM, Milos said:

Hello all,

 

I have question related to connecting Vision 280 with Modbus TCP zenon SCADA driver. I have experience with other PLC-s but not with Unitronics.

Please find attached config below:

image.png.792632fadc344e817c8df16b01c9d0e6.png

Below you can see zenon driver config and one variable config. I tried to see ML12 from program. Is this the way to directly call adress from SCADA or I missed some step?

sigma is PLC name, PLC IP is in range of PLC.

image.thumb.png.4a7baa6c62f0685e97c0aa6254be8df0.png

I believe you are missing socket connection after TCP/IP Card Init (I am not sure if it is required only if you are not using the standarconfig) . and the correct Offset is 20492, the 5000 in the documentation is an Hexadecimal value, and I have the hunch that zenon uses a decimal value:  5000h = 20480 DEC 20480 + 12 = 20492.

 

 

 

 

 

Link to comment
Share on other sites

6 hours ago, Milos said:

Thank you Fernando.

I will check with socket connection. Regarding adressing,  Vision 280 should be basic model so adressess listed in manual should be Decimal, for advanced is Hex. Anyway I will try.

Thank you one more time.

I think you are correct. Also i found another manual online that says ML statrs on 5100, you could try 5112 and see if that works

 

Link to comment
Share on other sites

  • MVP 2023

1.    I don't put any conditions on my SCAN_EX Modbus Slave block - 

image.png.d14c6d7399e7f42809d9b29ba5f0891e.png

 

2.  As Fernando pointed out, your net ID should be 255.

3.  All of the V280's memory is open to read via Modbus.  Rather than fighting to get the right offset for an ML read, try setting your offset to 0 to read MI 0 to establish a baseline that your communication works.   Set your Data Type to INT.  If that doesn't work try offset 1.

4.  Your "Data Block" is set to 0.  Should that be at least 1?

 

Otherwise, upload your program.

 

Joe T.

 

 

Link to comment
Share on other sites

  • 2 weeks later...

Thank you all for the advices. After a bit struggle I succeded :)

For the ID, I put 2 and it was OK, the tricky was for the DWORD bzte order, default is Big-Endian and it should be Little-Endian.

@Fernando Castro thank you for the advice to try with MI, after that I figured out that comm is ok and that I have problem with adressing. 

image.thumb.png.e0a160e5ef07582ef08a78c882319fcc.png

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.