Jean-Jacques Lubin Posted November 23, 2017 Report Share Posted November 23, 2017 I'm creating a new program for this system which is already wired up, the thermocouple is connected to the Port 2 of the V570. How do I read the data from the port and for the data to be converted into Degrees Celsius. Thanks JJ Link to comment Share on other sites More sharing options...
MVP 2023 Flex727 Posted November 23, 2017 MVP 2023 Report Share Posted November 23, 2017 If I'm not mistaken, the V200-18-E2B Snap-In module does not have thermocouple inputs. You'll need a V200-18-E3XB. Link to comment Share on other sites More sharing options...
MVP 2023 Ausman Posted November 23, 2017 MVP 2023 Report Share Posted November 23, 2017 Edited, I was stupid and didn't look at the description header! cheers, Aus Link to comment Share on other sites More sharing options...
MVP 2014 Simon Posted November 23, 2017 MVP 2014 Report Share Posted November 23, 2017 Hi JJ, I have a few questions: * When you say it is connected to Port 2 of the V570 - do you mean COM2? Does the thermocouple have a Serial/Modbus interface? * The post by Flex727 is correct, the E2B snap-in module doesn't take thermocouple inputs directly. It would need a signal transmitter, typically this converts the thermocouple interface to 4...20mA current signal. If you have a datasheet for the thermocouple and/or any photos of the device and the way youhave it wired up, please post. Link to comment Share on other sites More sharing options...
Jean-Jacques Lubin Posted November 24, 2017 Author Report Share Posted November 24, 2017 Hi Simon, Thanks for the quick reply. The equipment i'm working on has been wired by a previous company and we've been asked to re program the V570, to give them more options when they run their test. The thermocouple type J is connected to a Shinko temperature controller BSC2R0006 which has a serial output which is connected to V570 Port 2 as shown on the photos below, which could be COM2. The serial output is 4-20mA and type J thermocouple range is -200 to 1200 degC. I guess what i need to know if V570 port 2/com2 can read analog signal and how do we program on V570. If you can help that will be greatly appreciated. JJ Link to comment Share on other sites More sharing options...
Kikis Posted November 24, 2017 Report Share Posted November 24, 2017 Hi jean, 4-20mA is an analog signal and has nothing to do with the serial port. IO-V200-18-E2B snap-in module can take 4-20mA analog input, but this is not the way you have to proceed. From datasheet, i can see that Shinko's BSC2 temp. controller can communicate with external devices via RS485 using Modbus. Most probably they used this protocol in order to read and write parameters (PV, SV) via V570. Check the parameter values on the BSC2 to find out how serial connection is configured (communication protocol, speed, etc...). You can also remove the snap in module and check the DIP switches on the V570 to see if COM port 2 was set to RS485. Then we can provide more help. Link to comment Share on other sites More sharing options...
Jean-Jacques Lubin Posted November 28, 2017 Author Report Share Posted November 28, 2017 Kikis, Yes Shinko's BSC2 temp. controller serial connection for Modbus ASCII start Bit 1, Data Bit 7, Parity Even, Stop bit 1, and communication speed 38,400. V570 Com port 2is set to RS485. What I'll need to know now is how to put this in the ladder diagram. Hope you can help me, Thanks Link to comment Share on other sites More sharing options...
Kikis Posted November 29, 2017 Report Share Posted November 29, 2017 Hello Jean, Best way to understand how Modbus works with Unitronics is to watch the following webinar. There are also a lot of Modbus example programs included within Visilogic. Your V570 will be the master in the network, so you need the Modbus slave address table of the BSC2 to select the parameters you want to read or write to. Link to comment Share on other sites More sharing options...
Jean-Jacques Lubin Posted November 30, 2017 Author Report Share Posted November 30, 2017 Kikis, Thanks for the response, it did help. JJ Link to comment Share on other sites More sharing options...
Jean-Jacques Lubin Posted February 18, 2018 Author Report Share Posted February 18, 2018 Hello, I'm still having issues to connect and read the "PV" value of the Shinko Temperature controller using Modbus Protocol. The parameters set are the following; PLC - V570 Modbus ASCII Communication speed 19200bps Data bit/Parity 7 bits/Even Stop Bit 1 Slave ID #65 and Slave address 0100H and I have change the dip switches to RS485 on V570 Shinko Temperature controller Modbus ASCII Instrument number 65 Communication speed 19200bps Data bit/Parity 7 bits/Even Stop Bit 1 Response time 10ms See attached Shinko documents and a screen shot of the ladder diagram. When I try to read PV value I’m getting an error message of no communication established (Status Message goes from 4 to 5). I have been communicating with Shinko Japan and we have checked my wiring and settings all seemed to be ok. But they mentioned that the PLC need to send this command 020401000000F9 CrLf, This is where I'm not sure how do that. If you could help it would be greatly appreciated. Regards JJ serial communication shinko remp controller.pdf Link to comment Share on other sites More sharing options...
MVP 2023 Joe Tauser Posted February 18, 2018 MVP 2023 Report Share Posted February 18, 2018 The command they told you to send is not a Modbus ASCII protocol command. Modbus ASCII command strings all start with a ":" (hex 3A). Based on the document, I tend to believe that's the Shinko native protocol The help on RS485 can be misleading. You don't have to use 65 as a slave address. I'd start over and set the instrument to address 2, Modbus RTU, 19200 8 data No Parity 1 stop (19.2 8N1). Then set your V570 to match. Post your code so we can drill into the COM init block. Joe T. Link to comment Share on other sites More sharing options...
Jean-Jacques Lubin Posted February 19, 2018 Author Report Share Posted February 19, 2018 Joe, I have done the changes you suggested, which is good as now i'm not getting any error messages regarding communication as my status message is "0". But the return value at "MI 23" is fluctuating between 0 and 1, I need the value to return the PV display of the shinko Temp. controller value of 23 degrees or whichever the PV display is. As i'm logging that value into a Table and a Running curve. Attach is my code of my PLC program. thanks for your help. JJ PLasticorder PL200 v12.vlp Link to comment Share on other sites More sharing options...