I am rebuilding the controller of the line. My problem is that I need to install the length measureing with a 2500 ppr that countes up and down so I need to use both channel A and B. I cannot get the controller (SM70-J-RA22) to do its thing on the display. What ever I do the count just constantly increasese when input 0 or 1 is switched on.  Am I programming it right or is this the wrong  device for this job?. You help would be appreciated. It is a clever bit of kit so it should do it. Thank you for your help.

Link to comment
Share on other sites

Quote

I am sorry if I seem dim. All the jumpers are as factory and the inputs are active. I cannot find where to change the hardware config to shaft encoder unless it is in the programming. if so please point me in the right direction. This is the first time I/we have had this type of controller. We have used other plc systems which is madly expensive and this unit is ideal for this small application.

 

Link to comment
Share on other sites

Open Visilogic

       View

             HW_Configuration

                    Click on the LOWER box - FULL PART NUMBER   SM70-J-RA22

                             High Speed Inputs   Tab

                                        none - dropdown - choose the High Speed Function to use   ( A-B  shaft Encoder x 2)  and choose an ML  as the operand

 

                  Using any Analog Inputs and  Outputs      -- Open the tabs and set them up  -- and the related jumpers in the unit

 

    AND  -- Is the encoder   NPN or PNP outputs?      -- Set the NPN/PNP  Jumper accordingly -  And ALL inputs will be either PNP or NPN !

 

 

Link to comment
Share on other sites

Thank you all for your help.

Dan t's solution did the trick. I have the encoder input going into a STI (ML) with the shaft encoder into the ML0, ML1 is blank?. I am picking up ML0 into a A=B block with ML2 set as the target. The machine is a cut to length so when the guillotine cut to size the shaft encoder count needs to zero. I have never used these units before so it twisting me head. I have used mitsubisi, siemens and other controllers so sequencing and logic is not new to me. If I can get the hang of these controllers then there are other applications they will be used on.

Thanks again to all

Peter

Link to comment
Share on other sites

  • MVP 2023
10 minutes ago, peter leeming said:

If I can get the hang of these controllers

In case you don't know, Peter, under Visilogic's Help heading, there are numerous examples that will help you along the learning path.  Some may not be for your particular unit, but the principles are generally the same and can make things much easier to absorb.

cheers,

Aus

Link to comment
Share on other sites

  • MVP 2023

In the Hardware config section (under View) for the controller, have you noticed the High Speed Inputs (Reload) section?  Join the dots with the info in Help under Immediate: Update High-speed Input.  I think that will likely help to solve your headtwisting!

cheers,

Aus

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...