I'm not saying that's the problem, but that's the first thing I'd check. Try wiggling the cable at both ends and along the length while the PLC is in operation to see if you can induce the problem. If not, then you might look for a source of electrical interference, such as a nearby VFD or other poorly shielded RF source.

Do you also have a Snap-In module installed?

Link to comment
Share on other sites

  • MVP 2023
Just now, Guilherme said:

It's necessary install this Module?

No. There's two different types of I/O modules available - "Snap-In" modules and "Expansion" modules. Depending on your project requirements, you can have either or both. Sometimes the Snap-In modules can work lose and cause problems, so that is why I was asking.

Link to comment
Share on other sites

  • 1 month later...
On 3/25/2021 at 3:59 PM, Flex727 said:

No. There's two different types of I/O modules available - "Snap-In" modules and "Expansion" modules. Depending on your project requirements, you can have either or both. Sometimes the Snap-In modules can work lose and cause problems, so that is why I was asking.

The project contain 3 IO modules Digital, and I already tested the expansion cable. But the fails still happening 

Link to comment
Share on other sites

  • MVP 2023
11 hours ago, Guilherme said:

already tested the expansion cable

Does this mean it is a correct one like Flex has said?

Are the module interconnections all firmly seated.

Is the Power supply correctly applied everywhere and of sufficient capacity?

Set up logging of I/Os to see if the failure is attributable to the same one all the time, which would indicate a fault on that one.

In your photo it does not show the RUN S.C. leds on the first module. Is the RUN green like the others?

 

Link to comment
Share on other sites

  • MVP 2023

Quastions;

1 What expansion module used EX-A1X or EX-A2X?  EX-A2X is isolated and more stable.

2 How much W is power supply capacity? If it low - install NEW another one with more A on 24VDC outputs

3 Is it possible that on output present relay or valve coils without diode clamp?  If Yes - install diode clsmp to all coils

4 Is it some VFD installed near PLC - if Yes - please connect -24V power supply wire to machine GROUND (EARTH).

5 Is it possible that on some output present short circuit? And some times PLC  activate this output and restart PLC with error?

 

Link to comment
Share on other sites

  • 9 months later...

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...