Hi everyone.
I have tried to communicate with a MYCOM compressor that has a MAYEKAWA controller which in the manual says that it allows RS485 communication, I have been trying for 3 days without success.
The MAYEKAWA controller detects the requests made by the V1210 but when returning the information it arrives with a 5 in the message status.

Link to comment
Share on other sites

  • MVP 2023

Hi, i do not find full manual, but as i know - you must use correct wiring (four wire half duplex used) for MODBUS communication and set correct communication channel in panel setup menu.

I find modbus manual for new type of panels

https://mayekawa.com/americas/mna/downloads/pdf/CP Integration/MYPRO Touchplus/DEVICELISTMYPROTOUCHAREA.pdf

https://mayekawa.com/americas/mna/downloads/pdf/CP Integration/MYPRO Touch/MYPROTOUCHDeviceListMYPROTouchAreaManual.pdf

but you must use appropriate for your panel. 

 

  • Like 1
Link to comment
Share on other sites

  • MVP 2023

The manual makes reference to onboard termination resistors which I assume are set ok, and are also done correctly at the plc end.

I've said it before and will say it again, it is so much easier to do initial modbus work with the PC, to ascertain correct numbering requests and all possibilities available.  Don't forget Visilogic's numbering system can differ by 1.

cheers, Aus

  • Thanks 1
Link to comment
Share on other sites

Hello, thank you very much for your prompt response Gentlemen.
I want to thank AlexUT for providing the correct MAYEKAWA CP IV controller manual.
According to wiring it should be like the first image:

The data flow should be as follows but I am not very clear about this form of data flow, could you explain to me how to do it?

 

The number references should be the following, but I have called them decimal or hexadecimal but without success.

If you want to see the manual I will leave it here, again thanking AlexUT.

MAYEKAWA1.png

MAYEKAWA2.png

MAYEKAWA3.png

488091769_MayekavaMYPRO-CPIV_Manual-pdf-free.pdf

Link to comment
Share on other sites

  • MVP 2023

No worries at all.  I'm suggesting you use something like Modbus Poll or a similar program, which lets you easily communicate with the remote device to find what works and what doesn't.  Once you find exactly the best way to do things by using the PC, you can easily translate that method(s) into PLC use.  Trying to do it in the first place just using the PLC is very cumbersome.

Am I correct in assuming that you now have comms working ok, but are having trouble with the data layout?

cheers, Aus

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...