How can I convert DI/DO read as 16-bit words to coil status with Modbus 485?
Hello,
a customer is trying to read inputs and outputs on a Samba PLC using Modbus RS485.
They are using a Siemens Simantic S7 ET200 PLC to do so. But it can only read coils in range 0-9999.
The Samba digital outputs start from 16384 (4000h) and the digital inputs from 24576 (6000h).
The only thing they can read in the range above 9999 is 16 bit words with Modbus function 04.
The question is, how can they get the coil status information they need from the 16 bit word? Does anyone have a clue how to solve this? Comment from the customer below.
"That means we have to split the word with 16 bits into its individual bits and speculate if these individual bits contain the desired information that we need.
Where is the start address? Let's start with the address as you specified at 24576 and read in a data length of 10, With the normal approach, this would be the addresses 24576-24585 as bit operands, i.e. 10 individual bits.
Let's read it in as input words  and start at 24576 with a length of 10, this would also be the addresses 24576-24585 as words with 10x16 single bits.
 The problem for us now is where exactly is the information we need? Can we assume that the first 10 bits of the first word from address 24576 onwards also correspond to the bits you specify or every first bit of each word is the bit that contains the information?"
Any help would be appreciated.
Best regards Peter
  • PeterFukt changed the title to How can I convert DI/DO read as 16-bit words to coil status with Modbus 485?
As i see in siemens pdf - coil address is W#16  register - then it can be from 0000 to FFFF in hex.
Maybe issue is with correct numbering in modbus - 0 in unitronics +1 in standard modbus?
Please check this.
I've never used Siemens and don't know this PLC.  I don't know how they're trying at present, but it would appear they would have to be using a dedicated comms module.....ET 200SP, CM PTP.  If they're doing it somehow else which is perhaps native on the main cpu itself, then perhaps they could put in one of these modules.
Here's a scrnshot of what I see as very relevant from the module manual.  It looks like it should work RTU immediately.
cheers, Aus.