AAsher Posted August 25, 2022 Report Share Posted August 25, 2022 Using a V130 configured for TCP I am using an external device to continuously poll the state of a blocks of registers. This works fine for several days but occasionally will simply stop responding to modbus requests. I can ping the V130 and connect to it using Visilog so I know the IP address is setup correctly but no modbus activity is possible. Once I reboot the V130 everything works until it stops responding again after a few days. Any suggestions on what I should look for would be much appreciated. These are the TCP setup rungs Quote Link to comment Share on other sites More sharing options...
Gabriel Franco Posted August 25, 2022 Report Share Posted August 25, 2022 If you post your code, I can take a look. So far, make sure SB168 is set at power-up Quote Link to comment Share on other sites More sharing options...
AAsher Posted August 25, 2022 Author Report Share Posted August 25, 2022 36 minutes ago, Gabriel Franco said: If you post your code, I can take a look. So far, make sure SB168 is set at power-up Thanks Gabriel! I will set SB168 and watch what happens. It's intermittent but I should know in a few days if that solves the issue. Quote Link to comment Share on other sites More sharing options...
Fernando Castro Posted August 25, 2022 Report Share Posted August 25, 2022 I had a similar problem with one v700 ( just 1 from 100), never found the issue I added an internal reconnection function in the ladder logic monitoring if the socket status has no connection for like 3 minutes. But still haven't ran the PLC long enough to see if that solved the problem Quote Link to comment Share on other sites More sharing options...
MVP 2022 Ausman Posted August 25, 2022 MVP 2022 Report Share Posted August 25, 2022 @Cara Bereck Levy I must be missing a perfectly valid reason why SB168 doesn't default as set at power-up. We often have users not knowing about this, and it seems a bit odd to me that it has to be activated when it is actually an essential part of the process. cheers, Aus Quote Link to comment Share on other sites More sharing options...
MVP 2022 Flex727 Posted August 25, 2022 MVP 2022 Report Share Posted August 25, 2022 I've always wondered this too. I suspect the creators had something in mind that was a problem if it was set when it didn't need to be. Quote Link to comment Share on other sites More sharing options...
MVP 2022 kratmel Posted August 25, 2022 MVP 2022 Report Share Posted August 25, 2022 6 minutes ago, Flex727 said: I suspect the creators had something in mind that was a problem if it was set when it didn't need to be. This is not related to this topic, but in an empty project for some reason 0 is written in SI285 and I could not understand why this is done. Look at the STL view of the empty ladder program... Quote Link to comment Share on other sites More sharing options...
Fernando Castro Posted August 26, 2022 Report Share Posted August 26, 2022 2 hours ago, Ausman said: @Cara Bereck Levy I must be missing a perfectly valid reason why SB168 doesn't default as set at power-up. We often have users not knowing about this, and it seems a bit odd to me that it has to be activated when it is actually an essential part of the process. cheers, Aus SB 168 should be turned ON at power-up. It is OFF by default to preserve backwards compatibility with applications created previous to OS 4.70 B14. If SB 168 is ON, when the Ethernet link fails, the OS saves the Ethernet parameters and resets: • SB 142 Card Initialized • SBs 143-146 Socket initialized (Sockets 0-3) • SBs 147-150 Socket connected (Sockets 0-3) When the Ethernet link is reestablished, the O/S performs CARD INIT and SOCKET INIT for all 4 sockets according to the saved parameters. Speaking of that, this is one of those bits that does not work for v700 right? Quote Link to comment Share on other sites More sharing options...
MVP 2022 Ausman Posted August 26, 2022 MVP 2022 Report Share Posted August 26, 2022 Thanks Fernando, it's been so long since I first discovered this that I'd forgotten that part. Isn't it amazing what one finds when you look up Help! I don't know the answer re V700s. cheers, Aus Quote Link to comment Share on other sites More sharing options...
MVP 2022 Flex727 Posted August 26, 2022 MVP 2022 Report Share Posted August 26, 2022 11 hours ago, Fernando Castro said: Speaking of that, this is one of those bits that does not work for v700 right? I don't know the answer either, but I just checked and you do not get the compile warning on a V700 like you do with the other models. Quote Link to comment Share on other sites More sharing options...
Fernando Castro Posted August 26, 2022 Report Share Posted August 26, 2022 13 minutes ago, Flex727 said: I don't know the answer either, but I just checked and you do not get the compile warning on a V700 like you do with the other models. I just tested on v700 that bit is 0 on v700 even if you set the power up value to 1 and can not be set to 1 so the answer is that It is not compatible with v700 Quote Link to comment Share on other sites More sharing options...