draganjr Posted October 15, 2022 Report Share Posted October 15, 2022 Calculating FPM (feet per minute) or just Feet on a press. We have an old Comco Flexo Press from the early 90s, I think. We are removing the old Totalizer and replace it with a SM70-J-R20 with attached program. I am not sure if I am calculating the fottage correctly because it is different from the old totalizer. Could someone point me in the right direction please. And Thank you. ComcoTest_V3.vlp Quote Link to comment Share on other sites More sharing options...
MVP 2021 Ausman Posted October 15, 2022 MVP 2021 Report Share Posted October 15, 2022 Before anyone can help you on this, the thing that needs to be fully understood is the number of shaft rotations to output length. In your program, what is E-stop? Emergency or End? Why the different formulas?...Trying different maths to see if it matches up to old? There are many things odd in the structure of your program that invite comment, but the distance relationship is a must know before all else. cheers, Aus Quote Link to comment Share on other sites More sharing options...
Gabriel Franco Posted October 15, 2022 Report Share Posted October 15, 2022 It might be one of the following: 1. You are loosing pulses, since you are using normal inputs. Check shaft rpm against maximum allowable frequency from normal inputs. 2. Loss of precision due to formula calculations. Note that ML are integers, so decimals derived from calculations are truncated. Quote Link to comment Share on other sites More sharing options...
draganjr Posted October 16, 2022 Author Report Share Posted October 16, 2022 3 hours ago, Ausman said: Before anyone can help you on this, the thing that needs to be fully understood is the number of shaft rotations to output length. In your program, what is E-stop? Emergency or End? Why the different formulas?...Trying different maths to see if it matches up to old? There are many things odd in the structure of your program that invite comment, but the distance relationship is a must know before all else. cheers, Aus Yes. The last three rungs and the first few rungs are the important ones. The Stop/LED is not important at this time. It took 2.5 inches for one revolution of the shaft. The math it is using the same sensor for three different outputs (counters). We are trying to see if the math it good. What else do I need to do to capture a good foot? I will check a few more things and be right back. Thank you Dragan Quote Link to comment Share on other sites More sharing options...
draganjr Posted October 16, 2022 Author Report Share Posted October 16, 2022 At slow speed of the press 1 minute is about 507 rotations and according to the old counter it is about 106 feet. 5 rotations are about 1 foot. At high speed for 1 minute is 1749 rotations @ 364 feet. A * 2.5 / 12 The math is A = rotations of drive shaft. 2.5" is paper distance traveled in 1 rotation. than divided by 12 for the footage. Quote Link to comment Share on other sites More sharing options...
MVP 2021 Joe Tauser Posted October 16, 2022 MVP 2021 Report Share Posted October 16, 2022 6 hours ago, Gabriel Franco said: 2. Loss of precision due to formula calculations. Note that ML are integers, so decimals derived from calculations are truncated. Yep. Multiplying an integer by a floating point number is not a good idea. I would do this application in floating point (MF) land Your program is simple at this point so it won't be hard to modify. Look at the bottom of the Math functions for "Float". When your math isn't working right the best way to troubleshoot it is to use individual function blocks. You can't see inside a FORMULA block to look at the intermediate calculations. I've done a little hacking on your program for the first calculation, using Visilogic 9.8.94. You should be able to do the rest. Joe T. ComcoTest_V3 JT.vlp Quote Link to comment Share on other sites More sharing options...
draganjr Posted October 16, 2022 Author Report Share Posted October 16, 2022 2 hours ago, Joe Tauser said: Yep. Multiplying an integer by a floating point number is not a good idea. I would do this application in floating point (MF) land Your program is simple at this point so it won't be hard to modify. Look at the bottom of the Math functions for "Float". When your math isn't working right the best way to troubleshoot it is to use individual function blocks. You can't see inside a FORMULA block to look at the intermediate calculations. I've done a little hacking on your program for the first calculation, using Visilogic 9.8.94. You should be able to do the rest. Joe T. ComcoTest_V3 JT.vlp 241.02 kB · 0 downloads Thank you. I am on it. I will update. Quote Link to comment Share on other sites More sharing options...
draganjr Posted October 17, 2022 Author Report Share Posted October 17, 2022 So, I never missed around with MF, and I read about it but seems I cannot lower the decimal point down? See Attached. Reading 1.04E6 If 5 rotations = 1 foot, how can I use that for a ML in the math? Thank you again. Quote Link to comment Share on other sites More sharing options...
MVP 2021 Joe Tauser Posted October 17, 2022 MVP 2021 Report Share Posted October 17, 2022 I see you keep hours like I do. You need to do your scaling in MF registers to accommodate the decimal point you need, but as you can see they revert to exponential notation when the numbers get big. They only have 8 digits of precision. You'll need to convert them to MLs for display purposes. Have a look at the Float Convert functions in the Help, and post your code so I can hack a bit more. Joe T. Quote Link to comment Share on other sites More sharing options...
draganjr Posted October 17, 2022 Author Report Share Posted October 17, 2022 11 minutes ago, Joe Tauser said: I see you keep hours like I do. You need to do your scaling in MF registers to accommodate the decimal point you need, but as you can see they revert to exponential notation when the numbers get big. They only have 8 digits of precision. You'll need to convert them to MLs for display purposes. Have a look at the Float Convert functions in the Help, and post your code so I can hack a bit more. Joe T. Okay thank you. I was looking at after I sent the message. Not to sound dumb but code = program? Quote Link to comment Share on other sites More sharing options...
MVP 2021 Joe Tauser Posted October 17, 2022 MVP 2021 Report Share Posted October 17, 2022 Yes Quote Link to comment Share on other sites More sharing options...
draganjr Posted October 17, 2022 Author Report Share Posted October 17, 2022 5 minutes ago, Joe Tauser said: Yes Ok I found it and will test it out shortly. They are currently running, and the operator is a pain to work with. You are awesome. I work 12 hours and I am new at program, and this is my 5th press. The other presses are working great. This press is just different, and we really don't have a good place to put a sensor to measure the rotations. We are on the same shaft as the old one just a few feet away. ComcoTest_V5JT.vlp Quote Link to comment Share on other sites More sharing options...
MVP 2021 Joe Tauser Posted October 17, 2022 MVP 2021 Report Share Posted October 17, 2022 I'm always happy to help someone who's willing to put in the work to try to fix the problem themselves. Joe T. Quote Link to comment Share on other sites More sharing options...
draganjr Posted October 17, 2022 Author Report Share Posted October 17, 2022 18 minutes ago, Joe Tauser said: Yes I am a little confused on B and where do I get that from. A+B = C? A is Total Feet in MF, B =? and C will be my whole number to display. Quote Link to comment Share on other sites More sharing options...
MVP 2021 Joe Tauser Posted October 17, 2022 MVP 2021 Report Share Posted October 17, 2022 You'll see when you download it and look at the numbers. A is the MF you enter into the block and B will be the numbers to the left of the decimal, which is what you're interested in. C will be the decimal part. You may or may not be interested in this number. Joe T. Quote Link to comment Share on other sites More sharing options...
draganjr Posted October 17, 2022 Author Report Share Posted October 17, 2022 8 minutes ago, Joe Tauser said: You'll see when you download it and look at the numbers. A is the MF you enter into the block and B will be the numbers to the left of the decimal, which is what you're interested in. C will be the decimal part. You may or may not be interested in this number. Joe T. Oh okay I see. The image you see was not pulling up in the help file. I have not yet tried it but does B and C auto populate? Quote Link to comment Share on other sites More sharing options...
MVP 2021 Joe Tauser Posted October 17, 2022 MVP 2021 Report Share Posted October 17, 2022 Yes it does. Click on the green link to expand it. Joe T. Quote Link to comment Share on other sites More sharing options...
MVP 2021 Flex727 Posted October 17, 2022 MVP 2021 Report Share Posted October 17, 2022 8 hours ago, draganjr said: I have not yet tried it but does B and C auto populate? As a general rule (is this ALWAYS the case? I'm not totally sure) the pieces on the left side of a Function Block are inputs to the function and the pieces on the right are the outputs of the function, so yes they auto-populate. Quote Link to comment Share on other sites More sharing options...
draganjr Posted October 18, 2022 Author Report Share Posted October 18, 2022 On 10/17/2022 at 2:14 AM, Joe Tauser said: Yes it does. Click on the green link to expand it. Joe T. Update. It is working so far. I been off but will see the actual numbers tomorrow night. Using the B Output for the display. Thank you. Quote Link to comment Share on other sites More sharing options...
draganjr Posted October 18, 2022 Author Report Share Posted October 18, 2022 21 hours ago, Flex727 said: As a general rule (is this ALWAYS the case? I'm not totally sure) the pieces on the left side of a Function Block are inputs to the function and the pieces on the right are the outputs of the function, so yes they auto-populate. Yes it did. First time using it. Working great so far. Quote Link to comment Share on other sites More sharing options...
MVP 2021 Ausman Posted October 18, 2022 MVP 2021 Report Share Posted October 18, 2022 I'm pleased it looks like things are working out ok and fully agree with everything already said. But I also want to throw in something else. To me your sensor needs to have it's shaft revolutions to sensor triggering checked to confirm it is a fixed proportion over all speeds. This is easily done by looking at the sensor reading online whilst varying the shaft speed. eg 100 of output = X whilst 1000 of output = X x 10 and so on, over all the speed range possible. The reason is I wonder what metal your sensor target is made of (it looks to be aluminium) and whether the sensor is simply reading the steel screw that holds it in place on the shaft. With higher speeds it may not be triggering the sensor correctly, or long enough for it to be read correctly, if it is only sensing the screw. Not likely, but something to ensure is ok. Where the PLC controls the motor speed and also reads an output directly related to it, I always run this as a first check on this relationship by using a tiny bit of ladderwork for that machine that runs speed up and down in given steps and records results. I would also possibly slightly increase the sensor gap from the target. There's not much room there for any stray piece of waste etc floating around and getting caught. On the other hand, the way it is now.....it has to get into the tiny gap in the first place, which contradicts what I'm saying! Cheers, Aus Quote Link to comment Share on other sites More sharing options...
draganjr Posted October 18, 2022 Author Report Share Posted October 18, 2022 10 minutes ago, Ausman said: I'm pleased it looks like things are working out ok and fully agree with everything already said. But I also want to throw in something else. To me your sensor needs to have it's shaft revolutions to sensor triggering checked to confirm it is a fixed proportion over all speeds. This is easily done by looking at the sensor reading online whilst varying the shaft speed. eg 100 of output = X whilst 1000 of output = X x 10 and so on, over all the speed range possible. The reason is I wonder what metal your sensor target is made of (it looks to be aluminium) and whether the sensor is simply reading the steel screw that holds it in place on the shaft. With higher speeds it may not be triggering the sensor correctly, or long enough for it to be read correctly, if it is only sensing the screw. Not likely, but something to ensure is ok. Where the PLC controls the motor speed and also reads an output directly related to it, I always run this as a first check on this relationship by using a tiny bit of ladderwork for that machine that runs speed up and down in given steps and records results. I would also possibly slightly increase the sensor gap from the target. There's not much room there for any stray piece of waste etc floating around and getting caught. On the other hand, the way it is now.....it has to get into the tiny gap in the first place, which contradicts what I'm saying! Cheers, Aus Thank you for your feed back and I will look into it tomorrow night when I return. I tried several sensors and it's true some where not working right. I did move the current sensor over a little. It's metal and I also thought of hiw wide I should make the flag for the sensor. Quote Link to comment Share on other sites More sharing options...
draganjr Posted October 20, 2022 Author Report Share Posted October 20, 2022 On 10/18/2022 at 4:46 PM, Ausman said: I'm pleased it looks like things are working out ok and fully agree with everything already said. But I also want to throw in something else. To me your sensor needs to have it's shaft revolutions to sensor triggering checked to confirm it is a fixed proportion over all speeds. This is easily done by looking at the sensor reading online whilst varying the shaft speed. eg 100 of output = X whilst 1000 of output = X x 10 and so on, over all the speed range possible. The reason is I wonder what metal your sensor target is made of (it looks to be aluminium) and whether the sensor is simply reading the steel screw that holds it in place on the shaft. With higher speeds it may not be triggering the sensor correctly, or long enough for it to be read correctly, if it is only sensing the screw. Not likely, but something to ensure is ok. Where the PLC controls the motor speed and also reads an output directly related to it, I always run this as a first check on this relationship by using a tiny bit of ladderwork for that machine that runs speed up and down in given steps and records results. I would also possibly slightly increase the sensor gap from the target. There's not much room there for any stray piece of waste etc floating around and getting caught. On the other hand, the way it is now.....it has to get into the tiny gap in the first place, which contradicts what I'm saying! Cheers, Aus Good evening. The sensor I am using is a Sick IME12-04BPSZC0S. Switching freq is 2000 Hz. I am using metal not aluminum, I did have aluminum and was not working out well. I am assuming the higher the switching freq. the better. The sensor does need to be card thick close to read at high speeds. If not, it will not read at high speeds. What is a good sensor to use in your opinion for high-speed counting. I looked at other sensor we had in the shop, and this was the best one. When we jog the press at low speeds the counters all count the same. But again, at high speeds the new current counter falls back about 10 feet but gets greater over time. I will give the actual number towards the end of my shift at work. Thank you Ragan Quote Link to comment Share on other sites More sharing options...
MVP 2021 Joe Tauser Posted October 21, 2022 MVP 2021 Report Share Posted October 21, 2022 The best sensor for high speed is an encoder. You could put a toothed pulley on the main shaft and couple it to an encoder mounted next to it with a timing belt. The PLC has a high speed input on I0 designed for this. Joe T. Quote Link to comment Share on other sites More sharing options...
Fernando Castro Posted October 21, 2022 Report Share Posted October 21, 2022 58 minutes ago, Joe Tauser said: The best sensor for high speed is an encoder. You could put a toothed pulley on the main shaft and couple it to an encoder mounted next to it with a timing belt. The PLC has a high-speed input on I0 designed for this. Joe T. As Joe T. an encoder is the best way to measure speed/revolutions. On 10/20/2022 at 2:13 AM, draganjr said: a Sick IME12-04BPSZC0S. Switching freq is 2000 Hz. The switching frequency is not the problem. Is the way the sensor works. those are inductive sensors the sensing depends on the material and distance this one was designed to be used mounted "flush", and even being within the range (3.4 mm) technically only the tangent point of the bar (a very small area will be in the range of the sensor). so, it is no surprising to me that it doesn't sense well. I bet you that it will work better if its mounted parallel to the shaft and having some metal part attached or a longer screw pointing to the sensor Although the accuracy won't be as good as an encoder, you will have a pretty good repeatability even at higher speeds If you want to buy an encoder Sick has encoders that you can attach to the shaft, and they are like from very basic to very smart ones. Quote Link to comment Share on other sites More sharing options...