MODBUS ETHERNET READING TIMER VALUES (V350 SLAVE- UNISTREAM US5-B10-B1 MASTER)


Marcelo

Recommended Posts

Hi, I´m trying to read the preset and current value of TD10 from a VISION 350-35-TR34 using a UNISTREAM US5-B10-B1.

From the address table I got that the address are 6910 (preset value) and 7310(current value)

image.thumb.png.e376c33b718daba5fa847d48ccccfdf7.png

To read those values I did as follow:

image.thumb.png.bc7ccbca335c0b8e8ffe33f7f46c43ad.png

Where EQUIP1.t EST PRESET and EQUIP1.t EST CURRENT are INT32 variables. All other register reading works fine but cant make timer reading work, always get 0 value.

Any advice or help you could give me I will appreciate. Thanks in advance.

 

Link to comment
Share on other sites

Ok, thanks. To read TD10 preset I have to use the address C010h (49168), and to read TD10 current I need to use the address D010h (53264). Right?

Doing that still dosn´t work. I am missing something else?

Also, I am reading seconds? Or in wich format i am getting those timers values? Thanks

Link to comment
Share on other sites

  • MVP 2023
On 2/13/2023 at 1:58 PM, Marcelo said:

Also, I am reading seconds? Or in wich format i am getting those timers values?

Under the hood all Unitronics timers are 32 bit values of 0.01 second resolution.

Also, in hex TD 10 preset will be at C00Ah (49162) and current will be at D00Ah (53,258).

Joe T.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.