BastianPIA Posted August 25 Report Share Posted August 25 Good afternoon, I have a concern, I have some variables that I need to send from an mj20 et1 PLC, I am using the U90 ladder software, the question that is going to monitor all the variables contained in the program, but for this I need to send the states of the variables to a gateway through the Ethernet card,(It should be noted that I have the mj20 et1 module), I wanted to ask if there is a way to make a table with the variables that I want to send or if there is another way, Thank you. Quote Link to comment Share on other sites More sharing options...
MVP 2022 kratmel Posted August 26 MVP 2022 Report Share Posted August 26 You must read Help topic about possible Ethernet communication via Jazz2 PLC: Ethernet: Jazz 2 only You can run MODBUS master or slave. Please find sample U90 project for JZ20 in help menu MODBUS folder. Quote Link to comment Share on other sites More sharing options...
BastianPIA Posted August 28 Author Report Share Posted August 28 On 8/26/2023 at 12:48 AM, kratmel said: You must read Help topic about possible Ethernet communication via Jazz2 PLC: Ethernet: Jazz 2 only You can run MODBUS master or slave. Please find sample U90 project for JZ20 in help menu MODBUS folder. Ready I understand this, but how can I select which variables I can read, in other software there are tables where the variables I need are added, in u90 ladder I did not see this tool, are the marks that I have using automatically passed? thank you. Quote Link to comment Share on other sites More sharing options...
MVP 2022 kratmel Posted August 28 MVP 2022 Report Share Posted August 28 Any communication involves the interaction of two devices. Looking at the Jazz PLC, you can make it a Modbus TCP Slave and read everything you are interested in according to the table in the help. If you want the PLC to be the Master, you need to know the parameters (addresses) of the device cells where the PLC can write something. Your question about being able to send something over the Ethernet is a bit incomplete. Describe in detail what and where you need to transfer and read about the possible ways of interaction in PLC Jazz20. It is the cheapest of the Unitronics controllers and its networking capabilities are very limited. Therefore, either you use the existing Modbus TCP protocol, or you have to choose another more network-oriented Unistream PLC. Quote Link to comment Share on other sites More sharing options...
MVP 2022 Joe Tauser Posted August 29 MVP 2022 Report Share Posted August 29 On 8/25/2023 at 2:02 PM, BastianPIA said: I wanted to ask if there is a way to make a table with the variables Just to clarify, there is no "table". You can read the entire memory of the Jazz via Modbus; you just need to know the MI or MB addresses you are interested in. Can you describe your application in more detail? Are you reading from the PLC with SCADA software or another application (Modbus slave)? Or do you want the Jazz to write to another device (Modbus Master)? Joe T. Quote Link to comment Share on other sites More sharing options...
DanT Posted August 29 Report Share Posted August 29 Hi; To Expand a bit on Joe's comments. JAZZ - U90 Ladder does not have the type of tables you are looking for. You can saythat all MI or all MB are a table, but you are only in some tiny portion . You can read MI's and MB's individually , but many Modbus calls will be required to grab the data individually When there are several to be read or written to at one time, then Group them into a specific range of MI or MB so 1 Modbus call will read the range or write the range ( so consider this range as the table) If your program has the data all over the place, you can use the Store commands to put or read the data in the range for Modbus Read / Writes. ( do reads at the beginning and writes at the bottom of the ladder) DanT Quote Link to comment Share on other sites More sharing options...
BastianPIA Posted August 30 Author Report Share Posted August 30 Hello, thank you all for your answers, to describe a little more about my application, through the JZ20-J-R31 PLC (in charge of managing some motors and having some variables with the status of each motor that it commands) together with the card ethernet mj20 et1 I want to connect with a gateway through the Modbus TCP protocol to pass the data of the status variables and monitor the status of the motors online, in the cloud (very similar to a scada but on a smaller scale and more simple without control, only monitoring), so my question is, the PLC would work as a Slave and the gateway as a master, if I want to read the marks from M20-to M50, can I select somewhere this range of variables so that I can do it? read from the gateway, or would it depend on the gateway's configuration to read the variables I need. Thank you I hope I have been clear with my application, I have attached the configuration I have so far. Quote Link to comment Share on other sites More sharing options...
MVP 2022 Flex727 Posted August 30 MVP 2022 Report Share Posted August 30 Just a couple of comments: - You don't need SB 1 where you have placed it. - Do NOT place multiple unconnected logic threads in a single ladder rung. - Your timer will count 30 seconds one single time then the out bit will stay on as long as the PLC is powered on. Is that what you want? Quote Link to comment Share on other sites More sharing options...
BastianPIA Posted August 31 Author Report Share Posted August 31 17 minutes ago, Flex727 said: Solo un par de comentarios: - No necesita SB 1 donde lo ha colocado. - NO coloque múltiples subprocesos lógicos no conectados en un solo peldaño de escalera. - Su temporizador contará 30 segundos una sola vez y luego el bit de salida permanecerá encendido mientras el PLC esté encendido. ¿Es eso lo que quieres? I understand, I have already made the corrections, with respect to the program, I have not yet developed more of the logic hoping to resolve the question about how to read the variables from a Gateway, or with that configuration the PLC remains open to be read from the master, and that's it Is it up to this Master to choose which variables to read from the PLC? Quote Link to comment Share on other sites More sharing options...
MVP 2022 Flex727 Posted August 31 MVP 2022 Report Share Posted August 31 9 minutes ago, BastianPIA said: with that configuration the PLC remains open to be read from the master, and that's it Is it up to this Master to choose which variables to read from the PLC? Yes. 1 Quote Link to comment Share on other sites More sharing options...
MVP 2022 Joe Tauser Posted August 31 MVP 2022 Report Share Posted August 31 23 hours ago, BastianPIA said: if I want to read the marks from M20-to M50 I'm guessing these are motor status bits. If not please clarify. If so, then just write logic to turn on and off an MB with each one. Then your gateway will "read coils" and the address will be the same as the MB address and you can read them all in a block. Is the gateway a commercial product or something you've developed in house? Joe T. Quote Link to comment Share on other sites More sharing options...
gkovacs Posted Sunday at 12:46 PM Report Share Posted Sunday at 12:46 PM Hello, I would like to ask some help as I can see that in this topic there is plenty of information regarding how to use a JZ20-J-R16 as Modbus TCP Slave. I am able to read all the MI's and MB's, but I can't read I0-I7 (inputs) and O0 to O6 (outputs). (I am able to read analogue input as MI0). My question is how can I read the input and the output states through a Modbus TCP call? What I tried to read in I2 and I3: ReadDiscreteInputs(35003, 2) answer was: illegal data address The communication in bytes: modbus: sending 00 01 00 00 00 06 01 02 88 bb 00 02 modbus: received 00 01 00 00 00 03 01 82 02 I also tried: ReadCoils(35003, 2) answer was: illegal data address The communication in bytes: modbus: sending 00 02 00 00 00 06 01 01 88 bb 00 02 modbus: received 00 02 00 00 00 03 01 81 02 Any help is appreciated! Quote Link to comment Share on other sites More sharing options...
MVP 2022 Ausman Posted Sunday at 10:30 PM MVP 2022 Report Share Posted Sunday at 10:30 PM Have you fully read the entire Help file listed as MODBUS in U90 Help index? cheers, Aus Quote Link to comment Share on other sites More sharing options...
MVP 2022 Joe Tauser Posted Sunday at 10:40 PM MVP 2022 Report Share Posted Sunday at 10:40 PM Inputs start at Modbus address 04000 on a Jazz. Have you tried ReadCoils(4002),2 ? Joe T. Quote Link to comment Share on other sites More sharing options...
MVP 2022 Joe Tauser Posted Sunday at 10:51 PM MVP 2022 Report Share Posted Sunday at 10:51 PM @BastianPIA - You've followed the example to configure the Jazz for Modbus serial communications. I don't think this is what you want. Look in the Help for Modbus and click on the link for Modbus/TCP -> Ethernet: Jazz 2 only. You'll see there is a dialog box specifically for Ethernet communication setup. Joe T. Quote Link to comment Share on other sites More sharing options...
gkovacs Posted Monday at 06:08 AM Report Share Posted Monday at 06:08 AM Hello 7 hours ago, Ausman said: Have you fully read the entire Help file listed as MODBUS in U90 Help index? cheers, Aus Yes, I have fully read it and that is why I had my questions about Modbus. In the meanwhile, I was able to get out the needed information by misregarding the text about adding 30000 or 40000 to the vector address (which is simply not true because by using the different Modbus commands there is nothing to add). So, 7 hours ago, Joe Tauser said: Inputs start at Modbus address 04000 on a Jazz. Have you tried ReadCoils(4002),2 ? Joe T. ReadCoils(4001,2) works. And so does ReadDiscreteInputs(4001,2) giving the same result. The same is true for ReadCoils(5001,2) and ReadDiscreteInputs(5001,2). And that is a bit confusing as ReadDiscreteInputs is supposed to be available to read inputs, while ReadCoils is for setting and reading outputs. But anyway, the good news is that it works! Thanks for your reply! Quote Link to comment Share on other sites More sharing options...
MVP 2022 Ausman Posted Monday at 10:53 PM MVP 2022 Report Share Posted Monday at 10:53 PM 16 hours ago, gkovacs said: Yes, I have fully read it and that is why I had my questions about Modbus. The Slave Address table that Joe posted is part of the Help page I asked you about. Rather than do screenshots I thought it would be wise for you to know the page location for an indepth read. Help generally has all the info one needs, but sometimes does need deep digging. cheers, Aus Quote Link to comment Share on other sites More sharing options...