I have V350 problem. When viewing the watch window input status, if input 0 is turned on, all inputs turn on. Is this a problem others have seen?

Edited by cubcrazy
Tilted change
  • MVP 2023
Posted
2 hours ago, kratmel said:

Please read manual and check jumpers inside PLC. 

Do this first.

It's probably got something to do with whether you have the inputs set to sinking or sourcing and what you're applying to Input 0.  Are you applying +24V or a contact closure as referenced to 0V?

Joe T.

Posted
8 hours ago, kratmel said:

Please post V350 model #. Is it plc new or used?

Please read manual and check jampers inside PLC. 

Model # V350-35-TR20 . The unit was purchased new.

Posted
6 hours ago, Joe Tauser said:

Do this first.

It's probably got something to do with whether you have the inputs set to sinking or sourcing and what you're applying to Input 0.  Are you applying +24V or a contact closure as referenced to 0V?

Joe T.

I'm monitoring a mechanical pressure switch, when the switch closes it applies+24 Vdc to input 0. Some manufactures look at this as sourcing the input, others view it as sinking. 

Posted
53 minutes ago, Flex727 said:

Here is the relevant section from the installation guide:

image.thumb.png.b7f54d15eb568a20ccc01f996c66e2ab.png

Jumper 1 is in position (B) pnp sourcing and input is wired as shown for pnp input wiring. 

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.