  1. The Minimum USB DOK is 4 GB for Upgrades. Anything less will cause the UniStream to Brick - I have seen one do this - It had to be replaced.
  2. Hi Oobretenov; YOU MUST use the EX-RC1_IO.vlp example as your base program from the UniStream Examples because there are differences in MI registers being used from the EX-RC1 Examples in Visilogic. Rename the file when you have made configuration changes to suit your project. Did you configure the EX-RC1 _IO for your I/O Modules? Set the DIP Switches on the EX-RC1 Module for the address ( 2 and above) UniStream is at Address 1 by default Then do the Export file, and Import it into UniLogic. The Export file from the EX-RC1 tells UniStream what I/O Modules are connected. Make sure the ID number you set is the same as the DIP Switch setting on the EX-RC1, Leave the General Buffers Unchecked. Then do the the Export from UniLogic of the INPUT and OUTPUT files-- At the top of the properties --, and Import these back into the EX-RC1. The Export files FROM the UniStream back to the EX-RC1 set up the Structs for the Inputs and Outputs properly to synchronize with the I/O Structs in UniLogic. Be sure to put the files in the right Structs in the EX-RC1. Be sure to Setup CANBUS Com Parameters in BOTH the EX-RC1 and the UniStream to be the same Baud rate ! This is a separate setting in UniLogic. Be sure the Terminating Resistors ( 75 ohm) are on BOTH the UniStream Connect AND the EX-RC1 Connector The CANBUS is an isolated Communications system, It needs its own 24 VDC power. It does not draw power from the EX-RC1 Module. On the EX-RC1, The I/O COM Led is Green and Steady when the I/O Modules are running properly. On the EX-RC1, The BUS Com LED is on Steady when the CANBUS is communicating properly, else it flashes. Dant
  3. Hi Felix; If the unit is under warranty - less than 2 years old, contact support. They may cover it under warranty thru your distributor. Else -- buy a new one - maybe your distributor will give you a break.
  4. Hi; The Upper Right corner can take a Non Touch Image. The UniStream uses the Touch function in this corner to be able to get to the built in background functions of the UniStream Controller( like the 'I' Key on the Vision and M91 Series) When you touch this area, a menu will appear - UniApps -- the background system functions for Troubleshooting, Manual Communications setup, Upgrades, etc. Another feature is to take a Screen Shot of the current active user screen. Dan
  5. There is a guide in the pinned area of this forum: How Do I Perform a Full Re-install of VisiLogic? this was written some years ago, so Program Files can now be Program Files(x86) some additional notes: Before doing the above, check and BE SURE ...... Program Files or Program Files(x86) Unitronics Unitronics Visilogic_C -- MOVE any project files you have there - like in the Applications folder, then Delete the entire folder -- DO NOT Have PROJECT Folders here - They may get deleted during Uninstalls !! ( Applications folder is not a safe place to keep project files, store your projects elsewhere -- Visilogic Uninstall can automatically delete this folder) Save project files frequently using revision indexes I the names, so you can go back to a previous revision if necessary. ( In the end , the final project is kept, and the backups can be removed)
  6. Hi Juandiaza; Hardware setup -- Have you set the High Speed Inputs up for A-B encoder? Jumpers- Internal -- Is the Encoder PNP or NPN Output? Default is PNP, If NPN - Open unit, change JP12 to A( NPN) See the installation guide. Note: If Encoder is NPN, then JP12 set to NPN will cause ALL Inputs to be NPN If encoder is NPN, - Open Collector or Pull Up Resistors Internal? HMI Numeric Value tied to the MI you selected in Hardware setup. Dan
  7. Is this in the main routine? or in a subroutine? is the subroutine being called?
  8. Hi; I have interfaced a V1040 into a couple of Pi's. I used the TCP-RAW Method and it worked well. Sent Integer data between them to trigger the Pi Camera. Used Python 3 for all the programming. Took a bit of research and trial and error to get it going as some information out there is a bit incomplete or misleading. Also used the MODBUS TCP method - there is a Python based Modbus program out there. It works well. I has more flexibility in some ways.. I will get the code for both methods and post it in a day or so. Current project is connecting a Pi to a Blind(display dead) Lego NXT via USB - working, needs cleanup. Aim is to get it all working together ( Vision, Pi, NXT, and a PIFace Digital I/O interface.) Dan .
  9. What model SAMBA are you using. The -T20 and -R20 models do not support Thermocouples. Thermocouples produce very small voltages in relation to the temperature being measured. The 0-10V Analog inputs ( 10 Bit ) are not fine enough to read the millivolts generated. Thermocouples are supported on the -RA22 and -TA22 Models. The Installation Sheet describes the wiring for the various types. In the -RA22 and -TA22 thermocouple inputs is already converted and the value is stored as xxx.x degrees C or F
  10. Attached is a Simple Timer Demo to illustrate an ON Delay Timer and change the value from another screen( Timer Direct) or thru an MI ( using the Special Functions) Screen 1 shows the timer preset and current times Screen 2 is to change the timer preset from the keypad using a separate screen Screen 3 shows using an MI to change the Timer Value When using an MI to change a time, you must use the Function Blocks in the M90 and JAZZ See the last net of the program to see the Special Function set up, also refer to the Help and Functions for further details. Simple Timer -JZ10-11-R16.U90
  11. Big nets Review the STL code for the net and often the STL sets itself up a bit different than the way you think in the net. I have seen this. Sometimes re-writing the net helps, but, breaking the net up into smaller nets removes the problem and the logic comes through cleaner and clearer
  12. Hi Justas; I have looked at your program. You appear to be using the USB port for programming and COM 1 for Modbus, You cannot do this . The USB port is probably set for 115,200 and the Modbus is set for 9600 The Installation manual says : The USB port may be used for programming, OS download, and PC access. Note that COM port 1 function is suspended when this port is physically connected to a PC. Recommendations: . Add a 2nd Com Port to the PLC V100-17-RS4X or Setup the Ethernet port and program thru the Ethernet Port - nice feature in the V700. -- see below You Initialize the Modbus several times - 1 for each device. This Modbus Config is for this unit- the Master(Client) This is Modbus ID 1 - only need to do this once. You have to set up each device to a different Modbus Address. ID address 2 , etc. In the Modbus Read Holding registers, this is where you define the Server(Slave) address to read from.- Trim the program to work with 1 Modbus Slave unit to start, and get it working, then add the others in. Typical Ethernet Setup Line: --||-------PLC Name ----- TCP/IP Config ------ TCP Socket Init SB2 - Power up Set the IP address Socket 1, Port 20256, TCP,Slave In the Connectons, change Serial to Ethernet, and then favorite, and enter the PLC name, IP Address, and port 20256. Be sure the IP address is on the same network your PC is on, and is an unused IP. After setting up the PLC, do a PING from the PC to be sure you can see the PLC. DanT
  13. Hi; I did a test myself. Have you Set up the TCP Connect properly to look at the MI with the Slave Address? and is there an IP Address entered at the MI ? DanT
  14. Hi Assuming you have the JZ20-R16, you will need install the JZ-RS4 Module to the JAZZ to be able to work with MODBUS. ( You will be programming the JZ20 via the USB Port, and can go online with the JAZZ to troubleshoot your program) There is an Example program in HELP-Examples-MODBUS that will show the steps to setup MODBUS in the JAZZ-M90 Controllers ( You have to use the Special Functions Methods - See Help - MODBUS for further details) From the Description provides, the JAZZ will be the MODBUS Master . Look up the JZ-RS4 Installation manual to review it's settings and wiring. DanT
  15. Hi; Trying to connect to a Gardner Denver Airsmart Controller Comm Module. Serial Interface - RS232 works. Trying the MODBUS TCP UDP protocol on their ports 2000 and 2001 - no luck yet, we can ping the IP OK, just no connection for MODBUS Read Registers(3) Any one had experience with this unit? Dan
  16. Hi Ausman; Have you looked at DataExport - one of the Free Utilities from Unitronics Set it up - Serial or Ethernet to the V230 and capture the data table on a Schedule - say 24 Hours This can be run on a PC and left open all the time . It can capture the data table, save it to an Excel file and also email it. You may have to add the Ethernet Card to the V230,or via Modem.
  17. Hi Saragani; Do You Mean Visilogic? and he is using Windows, not Linux. Dan Thomas. Fred: Windows 7 updates up to date? Did you also upgrade the OS in the PLC? Dan
  18. Hi; Customer has a Siemens 353 Controller and needs to communicate to it via Modbus ( we are using Serial RTU) Unistream is the Master, 353 is the slave. Communications is working properly We can read bits from the 353 like the push buttons, after adjusting the addressing by 1 ( Siemens 342 = Unitronics 341) We are having trouble with the Integer registers, they are coming back blank. Siemens 40061 - 40066 are basic clock data and we cannot read that, let alone the data that we need. Anyone with experience with this controller? a few more clues? Dant
  19. Hi Arbellah; Had the same issue. You cannot change the value the MI assigned to the High Speed Counter in the IO-D16A3-TO16. I tried saving the count data an loading it back in after a power up, and tried in the Online mode to change the value of the MI. Neither worked. In my case, we ended up removing the module and using a V200-18-E5B ( on a V570) . In your case, you will have to consider using another V130 like the TR20 or TR34 or R34. I think this is something Unitronics should look at, or provide an explaination. Dan.
  20. Hi Rodney; I am not official Unitronics Support., but from years of working with Unitronics products and working with the support teams: Unitronics has not and will not provide any type of internal documentation regarding the design of their products. They have a decent warranty policy, and if this is the case, go that route. If the item is out of the warranty period, then get a new unit - it is probably the best solution in the end. Just because 1 component appears defective, does not mean there are others that have been damaged too. Trying to get the components and the soldering techniques required to work with surface mounted components on multilayered boards is now an art for the experienced and time consuming. Also, making these repairs nulls out any certifications the unit originally had. Dan
  21. Hi; Yes, Be sure you get the RS232 Model and Power supply. Also get and extra programming cable RS232-CB1 to connect to Com 2. Dan Thomas
  22. Hi We have these bar code scanners connected to V1040's in our shipping dept Motorola DS9028 RS232 to go into the PLC's - V1040's Com 2 Very flexible in codes being read. We use standard codes and 2 dimensional Q codes. Reliable. Dan Thomas
  23. HI; Any one had experience with the CPU RS485 Port with regard to workmode Protocol (Com1)? The behavior and set up for data receive is different than using the USB ports on the HMI for 3rd party protocols If you have an actual working program, , can you post the COM Secton. Dan
  24. Hi; I have used several Prolific USB serial Converters over the years with Win XP, and 7 And when I tried to use them on Win 8 they did not work, even with the updated files from Prolific. Seems there was a flaw in the chip, and also knock-offs of the chip. The WIN 8 drivers won't work with the older versions. Ended up getting a newer USB cable with WIN 8 drivers included. Chances are , that is your problem. -- Get a new USB serial converter with drivers for Win 8. STAR has one that I use. Dant
×
×